Forum

Share:
Notifications
Clear all

CE10 Modbus transmission time-out fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
347 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem CE10 Modbus transmission time-out fault in delta ME300 series drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Modbus transmission time-out occurs.

When the communication time exceeds the detection time for Pr.09-03 time-out.

Verify the wiring and grounding of the communication circuit. It is recommended
to separate the communication circuit from the main circuit, or wire in 90 degree
for effective anti-interference performance.

Check the cable and replace it if necessary.

Fault treatment parameter

Pr.09-02
0: Warn and continue operation

1: Fault and ramp to stop

2: Fault and coast to stop

3: No warning, no fault and continue operation

Reply
Share: