EoL1 fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
380 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem EoL1 fault in delta MH300 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Electronic thermal relay 1 protection (EoL1)

Electronic thermal relay 1 protection.The drive coasts to stop once it activates.

Pr.06-14 (if the output current is larger than 105% of motor 1 rated current again within 60 sec., the counting time reduces and is less than Pr.06- 14.)

The load is too large - Reduce the load.

Decrease low-speed operation time.
Replace the drive with a dedicated to VFD model.

Increase the motor capacity.