How can resolve problem uC fault in delta MH300 drive ?
1 Reply
Apr 28, 2022 5:53 am
Under current (uC)
Motor cable disconnection - Troubleshoot the connection between the motor and the load.
Fault treatment parameter
Pr.06-73
0: No function
1: warn and coast to stop
2: warn and ramp to stop by the 2 nd deceleration time
3: warn and continue operation
The load is too low. Check the load status. Check if the motor capacity matches the load.
This fault comes if you run drive with low rating motor as compare to drive or without motor.