Delta MS300 Series Drive
1
Posts
1
Users
0
Reactions
142
Views
Jun 22, 2024 8:57 am
Cause : Modbus transmission time-out comes when incorrect communication command from upper unit or malfunction caused by interference.
The CE10 fault in MS300 drive indicates an Modbus transmission time-out. This means the communication time exceeds the detection time for communication time-out.
- Check if the communication command is correct.
- Check if the setting for Pr.09-02 is the same as the setting for the upper unit.
- Check the cable and replace it if necessary.