Delta MS300 Series Drive
1
Posts
1
Users
0
Reactions
121
Views
Jun 22, 2024 8:55 am
Cause : Illegal data value comes when incorrect communication command from upper unit or malfunction caused by interference. This fault occurs when Pr.09-02=0 and the motor drive keeps running. The drive resets automatically when receiving the correct function code.
The fault CE3 indicates an Illegal data value error in Delta MS300 drive. This means the drive received a command that it doesn't understand or can't execute or data value is illegal.
- Check if the communication command is correct.
- Check if the setting for Pr.09-02 is the same as the setting for the upper unit.
- Check the cable and replace it if necessary.