Lv Low voltage fault in delta VFD EL-W series drive

2 Posts
1 Users
0 Reactions
749 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem Lv Low voltage fault in delta VFD EL-W series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Low voltage

The AC motor drive detects that the DC bus voltage has fallen below its minimum value.

1. Check whether the input voltage is in the AC motor
drive rated input voltage range.
2. Check for abnormal load on the motor.
3. Check for correct input power wiring to R-S-T (for
three-phase models) without phase loss.