Forum

Share:
Notifications
Clear all

oL1 Overload 1 fault in delta VFD EL-W series drive

2 Posts
1 Users
0 Reactions
518 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oL1 Overload 1 fault in delta VFD EL-W series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Overload 1

Internal electronic overload trip.

1. Check for possible motor overload.
2. Check the electronic thermal overload setting.
3. Replace the drive with a larger capacity model.
4. Reduce the current level so that the drive output
current does not exceed the value in the Motor Rated
Current (Pr.07.00).

Reply
Share: