Cause : Motor overload comes when a motor draws a current that exceeds its rated capacity for an extended period. This fault is typically a protective measure to prevent motor overheating or damage due to excessive mechanical load or electrical issues.

"Motor overload" fault in "drive" indicate that the motor draws more current than its rated capacity. This means load on the motor might be too high, causing the motor to draw excessive current.

Common Causes of Motor Overload

  • Excessive Load: Attempting to drive a load that is too heavy for the motor's rated capacity.
  • Mechanical Problems: Issues such as misalignment, bearing failure, or binding can increase the load on the motor.
  • Electrical Faults: Faulty power supply, incorrect wiring, or control system problems can lead to overloading.
  • Environmental Factors: High ambient temperatures or poor ventilation can contribute to overloading.

Troubleshooting Steps:

  1. Check for Overloading:

    • Inspect the mechanical load connected to the motor. Ensure it is not excessive or beyond the motor's rated capacity.
    • Look for any jammed, blocked, or misaligned mechanical components that could be causing the motor to work harder than normal.
  2. Check Motor and Drive Sizing:

    • Ensure that the motor and the Delta drive are properly sized for the application.
    • If the motor is undersized, consider upgrading to a larger capacity motor to handle the load.
  3. Inspect Motor Settings in the Drive:

    • Check the motor overload protection settings in the Delta drive. Make sure the rated motor current is set correctly according to the motor nameplate.
    • Ensure that the overload curve (if adjustable) is appropriate for the motor and application.
  4. Inspect for Electrical Issues:

    • Use a multimeter to measure the voltage on all three phases to ensure the power supply is stable and balanced.
    • If there are voltage fluctuations or phase imbalances, address those issues, as they can cause the motor to overload.
  5. Check for Mechanical Issues:

    • Inspect the motor bearings and shaft alignment.
    • Check for signs of excessive friction, binding, or wear in the motor or driven equipment.
  6. Monitor Motor Temperature:

    • Ensure that the ambient temperature around the motor is within its operating limits.
    • If the motor is operating in a high-temperature environment, improve ventilation or cooling to prevent overheating.
  7. Test the Motor:

    • If you suspect internal motor damage, such as a shorted winding, use an insulation resistance tester (megger) to check the motor windings.
    • If the windings are damaged, the motor may need to be repaired or replaced.