How can resolve problem F0001 Over Current fault in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over Current fault.

Possible Causes
1. Motor power (P0307) does not correspond to the inverter power (r0206)
2. Motor leads are too long
3. Motor lead short circuit
4. Earth faults

Diagnose & Remedy

Check the following:
1. Motor power (P0307) must correspond to inverter power (r0206)
2. Cable length limits must not be exceeded
3. Motor cable and motor must have no short-circuits or earth faults
4. Motor parameters must match the motor in use
5. Value of stator resistance (P0350) must be correct
6. Motor must not be obstructed or overloaded
7. Increase the ramp time
8. Reduce the boost level (V/f control: P1311 & P1312

 