Forum

Share:
Notifications
Clear all

F0003 UnderVoltage fault in siemens micromaster 430 or MM430 drive

2 Posts
1 Users
0 Reactions
422 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0003 Under Voltage fault in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Under Voltage - Main supply failed. Shock load outside specified limits.

Diagnose & Remedy

Check the following:
1. Supply voltage (P0210) must lie within limits indicated on rating plate
2. Supply must not be susceptible to temporary failures or voltage reductions
3. Enable kinetic buffering (P1240 = 2)

Reply
Share: