Forum

Share:
Notifications
Clear all

A0502 alarm in siemens micromaster 440 or MM440 drive

2 Posts
1 Users
0 Reactions
479 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A0502 alarm in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Overvoltage limit - Overvoltage limit is reached. This warning can occur during ramp down, if the dc-link controller is disabled (P1240 = 0).

This warning is generated,
- if the dc-link controller is disabled (P1240 = 0).
- if pulses are enabled
- if actual dc voltage r0026 > r1242.

Diagnosis & Remedy
If this warning is displayed permanently, check drive input voltage .

If this warning is displayed permanently, check drive input voltage .

 

Reply
Share: