F0005 fault in siemens micromaster 440 or MM440 drive

3 Posts
1 Users
0 Reactions
1,952 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0005 fault in siemens micromaster 440 or MM440 drive ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Inverter I2T.

- Inverter overloaded.
- Duty cycle too demanding.
- Motor power (P0307) exceeds inverter power capability (r0206).
- 100 % overload reached (refer to utilization r0036 )

Diagnosis & Remedy

Check the following:
- Load duty cycle must lie within specified limits.
- Motor power (P0307) must match inverter power (r0206)

Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Inverter I2T.

- Inverter overloaded.
- Duty cycle too demanding.
- Motor power (P0307) exceeds inverter power capability (r0206).
- 100 % overload reached (refer to utilization r0036 )

Diagnosis & Remedy

Check the following:
- Load duty cycle must lie within specified limits.
- Motor power (P0307) must match inverter power (r0206)