F0024 fault in siemens micromaster 440 or MM440 drive

2 Posts
1 Users
0 Reactions
320 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0024 fault in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Rectifier Over Temperature.

- Ventilation inadequate
- Fan inoperative
- Ambient temperature is too high.Diagnosis & Remedy

Check the following:
- Fan must turn when inverter is running
- Pulse frequency must be set to default value
- Ambient temperature could be higher than specified for the inverter