Mitsubishi FR-F Series- FR-F800, FR-F800-E, FR-F846-E2 & FR-F700 Drive
1
Posts
1
Users
0
Reactions
201
Views
Mar 30, 2024 6:29 am
Cause : Analog input fault comes when the inverter trips when a 30 mA or higher current or a 7.5 V or higher voltage is input to terminal 2 while the current input is selected by Pr.73 Analog input selection, or to terminal 4 while the current input is selected by Pr.267 Terminal 4 input selection.
- Check the Pr.73, Pr.267, and the voltage/current input switch settings.
- Either give a current less than 30 mA, or set Pr.73, Pr.267, and the voltage/current input switch to the voltage input and input a voltage.