Cause : Safety circuit fault comes when the inverter trips when a safety circuit fault occurs. The inverter trips if the either of the wire between S1 and SIC or S2 and SIC becomes non-conductive while using the safety stop function.
- When not using the safety stop function, the inverter trips when the shorting wire between terminals S1 and PC or across S2 and PC is disconnected.
- Check that the safety relay module or the connection has no fault when using the safety stop function.
- Check if the shorting wire between S1 and PC or between S2 and PC is disconnected when not using the safety stop function.
- When using the safety stop function, check that wiring of terminal S1, S2 and SIC is correct and the safety stop input signal source such as a safety relay module is operating properly. Refer to the Safety stop function instruction manual for causes and countermeasures.
- When not using the safety stop function, short across terminals S1 and PC and across S2 and PC with shorting wires.