Cause : Measured resistance has exceeded the parameter range comes when the value being used for motor stator resistance is too high or that an attempt to do a test involving measuring motor stator resistance has failed.
- The maximum for the stator resistance parameters is generally higher than the maximum value that can be used in the control algorithms.
- If the value exceeds (VFS / v2) / Full Scale Current Kc (11.061), where V FS is the full scale DC bus voltage then this trip is initiated.
- Check that the value that has been entered in the stator resistance does not exceed the allowed range.
- Check the motor cable / connections.
- Check the integrity of the motor stator winding using a insulation tester.
- Check the motor phase to phase resistance at the drive terminalsCheck the motor phase to phase resistance at the motor terminals.
- Ensure the stator resistance of the motor falls within the range of the drive model.
- Select fixed boost mode (Pr 05.014 = Fixed) and verify the output current waveforms with an oscilloscope.
- Replace the motor.