Forum

Share:
Notifications
Clear all

A142 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
332 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : In position - timer monitoring comes when the "in position - exact stop window" was not reached within the time specified in "in position - timer monitoring":

  • In position - exact stop window (machine data 17) too small.
  • In position - timer monitoring (machine data 16) too short.
  • Position controller or speed controller not optimized.
  • Mechanical causes.

Follow these steps to correct the fault:

  1. Check and correct the machine data.
  2. Optimize the position controller or speed controller.
  3. Check the mechanical system.
Share: