Siemens SIMOVERT Master Drive
1
Posts
1
Users
0
Reactions
272
Views
Jun 29, 2024 4:58 am
Cause : In position - timer monitoring comes when the "in position - exact stop window" was not reached within the time specified in "in position - timer monitoring":
- In position - exact stop window (machine data 17) too small.
- In position - timer monitoring (machine data 16) too short.
- Position controller or speed controller not optimized.
- Mechanical causes.
Follow these steps to correct the fault:
- Check and correct the machine data.
- Optimize the position controller or speed controller.
- Check the mechanical system.