cause : Configuration error comes when the configuration for encoder 2 is incorrect or Re-parameterization between fault/alarm is not permissible.
Alarm value (r2124, interpret decimal):
1: Re-parameterization between fault/alarm is not permissible.
419: When the fine resolution Gx_XIST2 is configured, the encoder identifies a maximum possible absolute position
actual value (r0483) that can no longer be represented within 32 bits.
Re alarm value = 1:
No re-parameterization between fault/alarm.
Re alarm value = 419:
Reduce the fine resolution (p0419) or deactivate the monitoring (p0437.25), if the complete multiturn range is not required.