Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
180
Views
Feb 16, 2024 12:14 pm
Cause : SI Motion P1- Steady-state (static) 1 signal at the F-DI for safety-relevant acknowledgement comes when a logical 1 signal is present at the F-DI configured in p10006 for more than 10 seconds. If, at the F-DI no acknowledgment was performed for safe acknowledgment, then a steady-state logical and 0 signal must be present. This avoids unintentional safety-relevant acknowledgement (or the "Internal Event Acknowledge" signal) if a wire breaks or one of the two digital inputs bounces.
Set the fail-safe digital input (F-DI) to a logical 0 signal (p10006).