Forum
Notifications
Clear all
How to resolve fault F01600 in G120C ?
2 Users
0 Reactions
Topic starter
(@neeraj)
Eminent Member
[#20372]
i have siemens g120c drive and its showing fault F01600, can you suggest how to correct this fault and also what are the cause of this fault
1 Reply
Admin
(@click2electro)
Member
Fault F01600 in SINAMICS G120C indicates a "Safety Integrated: STOP A initiated" error, often caused by a discrepancy in Safe Torque Off (STO) terminals or a Profisafe communication error.
To resolve, power cycle the drive (OFF/ON), check safety wiring (STO terminal 1&2), verify Profisafe telegrams, and check for associated faults like F01611
Reply