Siemens SINAMICS G120 Drive
420
Feb 16, 2024 5:19 pm
Cause : Analog sensor channel B failed comes when the input voltage of the analog sensor is outside the permissible limits.
2: Input voltage outside the measuring range set in (p4675).
3: The absolute value of the input voltage has exceeded the range limit (p4676).
Re alarm value = 1:
- check the output voltage of the analog sensor.
Re alarm value = 2:
- check the voltage setting for each encoder period (p4675).
Re alarm value = 3:
- check the range limit setting and increase it if necessary (p4676).