Forum

Share:
Notifications
Clear all

Er-08 alarm code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
45 Views
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Rated Slip Error comes when motor data entered during Auto-Tuning was incorrect or results from Auto Tuning are outside the parameter setting range or the tuning process took too long.

  1. Restart Auto-Tuning and enter the correct information.
  2. Check and correct faulty motor wiring.
  3. Perform Rotational Auto-Tuning.
  4. The load was too high during Rotational Auto-tuning.
  5. Disconnect the motor from machine and restart Auto-Tuning. If motor and load cannot be uncoupled make sure the load is lower than 30%.
  6. If a mechanical brake is installed, make sure it is fully lifted during tuning
Share: