Cause : Acceleration Error comes when the motor did not accelerate for the specified acceleration time or torque limit when motoring is too low (L7-01 and L7-02).
- The load was too high during Rotational Auto-Tuning.
- Increase the acceleration time (C1-01).
- Disconnect the machine from the motor if possible.
- Check L7-01 and L7-02 settings.
- Increase the setting.
- Disconnect the motor from machine and restart Auto-Tuning. If motor and load cannot be uncoupled make sure the load is lower than 30%.