Yaskawa E7, G7, GA800 & GA500 Drive
444
Mar 19, 2024 12:16 pm
Cause : Heatsnk Overtemp comes when the temperature of the Inverter's cooling fins exceeded the setting in L8-02 or the overheat protection level.
- The ambient temperature is too high. Install a cooling unit.
- There is a heat source nearby. Remove the heat source.
- The Inverter's cooling fan has stopped.
- Replace the cooling fan.
- A short-circuit between +V, -V, and AC terminals occurred.
- Overload in the control circuit terminal.
- Make sure that incorrect wiring has not been done.
• Check the resistance and wiring for the frequency setting potentiometer, etc. (Check that the cur- rent for terminals +V and –V is 20 mA or less.) - The Inverter's cooling fan has stopped.
• The heatsink is clogged.
• Replace the cooling fan.