Cause : Terminal Board Mismatch Error comes when the converter or the removable terminal block with parameter backup was replaced. The converter was replaced (but the removable terminal block with parameter backup was not replaced).
- Set A1-03 to 5550 to load the parameter settings stored in the terminal board to the drive.
- Initialize parameters after drive replacement by setting A1-03 to 2220 or 3330.