A1106 / F1107 Slot A enc. A cable disconnection Encoder channel A signal is not detected correctly. fault in WEG CFW900 Drive
These codes indicate a Slot A Encoder Channel A Cable Disconnection. This means the drive lost the primary positioning pulse signal from the encoder.
- Broken or disconnected signal cable.
- Encoder connection error.
- Encoder has no power supply.
Note: This check can be disabled by setting parameter C5.n.6.2 (where n is the slot index where the accessory is installed).
Verify the physical and electrical integrity of the encoder channel A cabling. Check terminal connections and verify the encoder auxiliary power supply voltage.
