Digitax ST Drive Fault Codes (2026) – Comprehensive 2026 troubleshooting guide for the Nidec Control Techniques Digitax ST servo drive. Learn to interpret mnemonic trips like OI.AC, Enc1, and HF hardware faults.
The Nidec Control Techniques Digitax ST is a high-dynamic response servo drive designed for pulse-duty applications requiring high peak torque and rapid acceleration. Although now part of a mature product line, it remains widely used in 2026 for indexing, pick-and-place, and synchronized motion systems. When the drive identifies a problem, it stops the motor and displays a mnemonic trip code—an abbreviated English string such as OI.AC (Overcurrent) or Enc1 (Encoder 1 Fault).
This guide provides the diagnostic framework to help you interpret these codes, manage the drive’s two SM-option slots, and resolve trips to maintain high-precision motion timing.
Digitax ST Fault Codes Reference Table
Below is the reference list of trips for the Digitax ST. Because this is a servo drive, many trips are related to position feedback and high-speed current loop stability. Please locate the code appearing on your drive’s LED display.
| Fault Code and Meaning | Cause and Remedy |
| OI.AC / 3 Instantaneous output over current detected | Cause: Over current threshold exceeded (Kc/0.45). Acceleration/deceleration rate is too short. Remedy:
| br.th / 10 Braking resistor thermistor temperature monitoring fail | Cause: Braking resistor issue or incorrect parameter setting. Remedy:
| C.Acc / 185 SMARTCARD trip: Read / Write fail | Cause: SMARTCARD is not writing data to data location 500 to 999. Remedy:
| C.boot / 177 SMARTCARD trip: Menu 0 parameter modification not saved | Cause: Necessary file not created on SMARTCARD. A write to menu 0 was initiated via keypad with Pr 11.42 set to auto(3) or boot(4). Remedy:
| C.bUSY / 178 SMARTCARD trip: Card busy | Cause: SMARTCARD cannot perform the required function as it is being accessed by a Solutions Module. Remedy: Wait for the Solutions Module to finish accessing the SMARTCARD and then re-attempt the required function. |
| C.Chg / 179 SMARTCARD trip: Data location already contains data | Cause: Attempting to write to a location that is not empty. Remedy:
| C.cPr / 188 SMARTCARD trip: Value mismatch | Cause: The values stored in the drive and the values in the data block on the SMARTCARD are different. Remedy: Press the red reset button. |
| C.dAt / 183 SMARTCARD trip: Data location empty | Cause: Data location specified does not contain any data. Remedy: Ensure data block number is correct. |
| C.Err / 182 SMARTCARD trip: Data is corrupted | Cause: Corrupted data on card. Remedy:
| C.Full / 184 SMARTCARD trip: Card full | Cause: No space left on SMARTCARD. Remedy: Delete a data block or use different SMARTCARD. |
| cL2 / 28 Analog input 2 current loss | Cause: Current signal loss in current mode. Remedy: Check analog input 2 (terminal 7) current signal is present (4-20 mA, 20-4 mA). |
| cL3 / 29 Analog input 3 current loss | Cause: Current signal loss in current mode. Remedy: Check analog input 3 (terminal 8) current signal is present (4-20 mA, 20-4 mA). |
| CL.bit / 35 Trip initiated from control word | Cause: Trip initiated via Pr 6.42. Remedy: Disable the control word by setting Pr 6.43 to 0 or check setting of Pr 6.42. |
| C.OPtn / 180 SMARTCARD trip: Solutions Modules difference | Cause: Solutions Modules installed are different between source drive and destination drive. Remedy:
| C.Prod / 175 SMARTCARD trip: Incompatible product | Cause: The data blocks on the SMARTCARD are not compatible with this product. Remedy:
| C.Rdo / 181 SMARTCARD trip: Read Only bit set | Cause: Card is read-only. Remedy:
| C.rtg / 186 SMARTCARD trip: Rating difference | Cause: Voltage and/or current rating of the source and destination drives are different. Remedy: Press the red reset button. Note: Drive rating dependent parameters (RA coding) will not be transferred or will be set to default. |
| C.SLX / 172, 173, 174 Error transferring user program | Cause: Error during transfer from Solutions Module to SMARTCARD (or vice versa). Remedy: See section 10.2.8 SM-Applications Modules And Motion Processors program to/from SMARTCARD transfer system. |
| C.TyP / 187 SMARTCARD trip: Parameter set not compatible | Cause: SMARTCARD parameter set not compatible with drive. Remedy:
| dESt / 199 Parameter writing conflict | Cause: Two or more parameters are writing to the same destination parameter. Remedy: Set Pr xx.00 = 12001 check all visible parameters in the menus for duplication. |
| EEF / 31 EEPROM data corrupted | Cause: Serial comms will timeout with remote keypad on the drive RS485 comms port. Remedy: This trip can only be cleared by loading default parameters and saving parameters. |
| EnC1 / 189 Drive encoder trip: Power supply overload | Cause: Encoder power supply overload. Remedy: Check encoder power supply wiring and encoder current requirement (Max 200 mA @ 15 V, or 300 mA @ 8 V and 5 V). |
| EnC2 / 190 Drive encoder trip: Wire break | Cause: Wire break detected on terminals 1 & 2, 3 & 4, 5 & 6. Remedy:
| EnC3 / 191 Drive encoder trip: Phase offset incorrect | Cause: Phase offset incorrect while running. Remedy:
| EnC4 / 192 Drive encoder trip: Comms failure | Cause: Feedback device comms failure. Remedy:
| EnC5 / 193 Drive encoder trip: Checksum or CRC error | Cause: Checksum or CRC error detected. Remedy:
| EnC6 / 194 Drive encoder trip: Encoder error indication | Cause: Encoder has indicated an error. Remedy:
| EnC7 / 195 Drive encoder trip: Initialization failed | Cause: Initialization failed. Remedy:
| EnC8 / 196 Drive encoder trip: Auto configuration failed | Cause: Auto configuration on power up requested and failed. Remedy:
| EnC9 / 197 Drive encoder trip: Position feedback selection error | Cause: Selected position feedback is from a Solutions Module slot which does not have a module installed. Remedy: Check setting of Pr 3.26 (or Pr 21.21). |
| EnC10 / 198 Drive encoder trip: Phasing failure | Cause: Encoder phase angle (Pr 3.25 or Pr 21.20) is incorrect. Remedy:
| EnC11 / 161 Drive encoder trip: Alignment failure (SINCOS) | Cause: Alignment failure of analog signals (SINCOS) with digital count. Usually due to noise. Remedy:
| EnC12 / 162 Drive encoder trip: Hiperface ID failure | Cause: Hiperface encoder type could not be identified during auto-configuration. Remedy:
| EnC13 / 163 Drive encoder trip: EnDat turns error | Cause: Number of encoder turns read during auto-configuration is not a power of 2. Remedy: Select a different type of encoder. |
| EnC14 / 164 Drive encoder trip: EnDat comms bits error | Cause: Number of comms bits defining the encoder position within a turn is too large. Remedy:
| EnC15 / 165 Drive encoder trip: PPR calculation error | Cause: Periods per revolution calculated is < 2 or > 50,000. Remedy:
| EnC16 / 166 Drive encoder trip: EnDat comms bits limit | Cause: Number of comms bits per period for a linear encoder exceeds 255. Remedy:
| EnC17 / 167 Drive encoder trip: SINCOS PPR error | Cause: Periods per revolution for rotary SINCOS encoder is not a power of two. Remedy:
| ENP.Er / 176 Electronic nameplate data error | Cause: Data error from electronic nameplate stored in selected position feedback device. Remedy: Replace feedback device. |
| Et / 6 External trip from input on terminal 31 | Cause: Triggered by external input. Remedy:
| HF01 – HF24 Data processing / Hardware errors | Cause: Internal Hardware or Software processing error (CPU, DMAC, Illegal instruction, Watchdog, Heap overflow, etc). Remedy: Hardware fault – return drive to supplier. |
| HF25 Current feedback offset error | Cause: Hardware fault. Remedy:
| HF26 Soft start relay failed to close, soft start monitor failed or braking IGBT short circuit at power up | Cause: Hardware fault. Remedy:
| HF27 Power stage thermistor 1 fault | Cause: Hardware fault. Remedy:
| HF29 Control board thermistor fault | Cause: Hardware fault. Remedy:
| HF30 DCCT wire break trip from power module | Cause: Hardware fault. Remedy:
| It.AC (Trip 20) Output current overload timed out (I²t) | Cause: Accumulator value reached limit (Pr 4.19). Load jammed, sticking, or incorrect motor parameters. Remedy:
| It.br (Trip 19) Braking resistor overload timed out (I²t) | Cause: Braking resistor overload. Accumulator value can be seen in Pr 10.39. Remedy:
| O.CtL (Trip 23) Drive control board over temperature | Cause: Control board temperature exceeded limits. Remedy:
| O.ht1 (Trip 21) Power device over temperature based on thermal model | Cause: Power device thermal model limit reached. Remedy:
| O.ht2 (Trip 22) Heatsink over temperature | Cause: Heatsink temperature too high. Remedy:
| O.ht3 (Trip 27) Drive over-temperature based on thermal model | Cause: Thermal model limit reached. The drive will attempt to stop the motor before tripping. Remedy:
| OI.AC (Trip 3) Instantaneous output over current detected | Cause: Over current threshold is Kc/0.45. Short circuit, insulation failure, or incorrect loop gains. Remedy:
| OI.br (Trip 4) Braking transistor over-current detected | Cause: Short circuit protection for the braking transistor activated. Remedy:
| O.Ld1 (Trip 26) Digital output overload | Cause: Total current drawn from 24 V supply and digital outputs exceeds 200 mA. Remedy:
| O.SPd (Trip 7) Motor speed has exceeded the over speed threshold | Cause: Speed exceeded threshold in Pr 3.08. Remedy:
| OV (Trip 2) DC bus voltage has exceeded the peak level or maximum continuous level | Cause: Deceleration too fast, supply disturbances, or motor insulation failure. Remedy:
| PAd (Trip 34) Keypad has been removed when receiving speed reference from keypad | Cause: Keypad removed during operation. Remedy:
| PH (Trip 32) AC voltage input phase loss or large supply imbalance detected | Cause: Phase loss or imbalance. Load level must be between 50 and 100% for trip to occur. Remedy:
| PS (Trip 5) Internal power supply fault | Cause: Hardware fault or module issue. Remedy:
| PS.10V (Trip 8) 10 V user power supply current greater than 10 mA | Cause: Overload on 10V rail. Remedy:
| PS.24V (Trip 9) 24V internal power supply overload | Cause: Total user load of drive and Solutions Modules exceeded internal 24V limit. Remedy:
| PSAVE.Er (Trip 37) Power down save parameters in the EEPROM are corrupt | Cause: Power removed while saving parameters. Remedy:
| rS (Trip 33) Failure to measure resistance during autotune | Cause: Measurement failure. Remedy:
| SAVE.Er (Trip 36) User save parameters in the EEPROM are corrupt | Cause: Power removed when user parameters were being saved. Remedy:
| SCL (Trip 30) Drive RS485 serial comms loss to remote keypad | Cause: Connection loss. Remedy:
| SLX.dF (Trip 204, 209) Solutions Module slot X trip: Type installed in slot X changed | Cause: Module configuration changed. Remedy:
| SLX.Er (Error 1) Encoder power supply overload | Cause: Current requirement > 200mA (15V) or 300mA (8V/5V) or Excitation output short (Resolver). Remedy:
| SLX.Er (Error 2) Wire break | Cause: Feedback signal wire break. Remedy:
| SLX.Er (Error 3) Phase offset incorrect while running | Cause: Noise or mechanical mounting issue. Remedy:
| SLX.Er (Error 4) Feedback device communications failure | Cause: Comms failure. Remedy:
| SLX.Er (Error 5) Checksum or CRC error | Cause: Data corruption. Remedy:
| SLX.Er (Error 6) Encoder has indicated an error | Cause: Internal encoder error. Remedy:
| SLX.Er (Error 7) Initialisation failed | Cause: Setup failure. Remedy:
| SLX.Er (Error 8) Auto configuration on power up has been requested and failed | Cause: Configuration failed. Remedy:
| SLX.Er (Error 9) Motor thermistor trip | Cause: Motor overheated or continuity issue. Remedy:
| SLX.Er (Error 10) Motor thermistor short circuit | Cause: Short circuit. Remedy:
| SLX.Er (Error 11) Failure of the sincos analog position alignment / Poles not compatible | Cause: Alignment or compatibility issue. Remedy:
| SLX.Er (Error 12) Encoder type could not be identified during auto-configuration | Cause: Identification failure. Remedy:
| SLX.Er (Error 13) Number of encoder turns read from the encoder during auto-configuration is not a power of 2 | Cause: Incorrect turns data. Remedy:
| SLX.Er (Error 14) Number of comms bits defining the encoder position is too large | Cause: Configuration issue. Remedy:
| SLX.Er (Error 15) Calculated periods per revolution either <2 or >50,000 | Cause: Auto-configuration data out of range. Remedy:
| SLX.Er (Error 16) The number of comms bits per period for a linear encoder exceeds 255 | Cause: Configuration issue. Remedy:
| SLX.Er (Error 74) Solutions Module has overheated | Cause: Over temperature. Remedy:
| SLX.Er (Error 39) User program stack overflow | Cause: Application module software error. Remedy:
| SLX.Er (Error 40) Unknown error | Cause: Internal error. Remedy:
| SLX.Er (Error 41-44) Parameter Access Error | Cause: 41: Does not exist, 42: Write to read-only, 43: Read from write-only, 44: Value out of range. Remedy:
| SLX.Er (Error 47) Synchronisation lost with CTSync Master | Cause: Sync loss. Remedy:
| SLX.Er (Error 48) RS485 not in user mode | Cause: Port configuration issue. Remedy:
| SLX.Er (Error 50) Maths error – divide by zero or overflow | Cause: Program math error. Remedy:
| SLX.Er (Error 51) Array index out of range | Cause: Program indexing error. Remedy:
| SLX.Er (Error 53) DPL program incompatible with target | Cause: Compiled for different hardware. Remedy:
| SLX.Er (Error 54) DPL task overrun | Cause: Task taking too long to execute. Remedy:
| SLX.Er (Error 59) Drive rejected application module as Sync master | Cause: Sync configuration rejected. Remedy:
| SLX.Er (Error 60) CTNet hardware failure | Cause: Hardware failure. Remedy:
| SLX.Er (Error 61-63) CTNet Configuration Error | Cause: 61: Invalid config, 62: Invalid baud-rate, 63: Invalid node ID. Remedy:
| SLX.Er (Error 64) Digital Output overload | Cause: Overload on module outputs. Remedy:
| SLX.Er (Error 75) Hardware unavailable | Cause: Module hardware issue. Remedy:
| SLX.Er (Error 76) Module type cannot be resolved / not recognized | Cause: Compatibility or identification issue. Remedy:
| SLX.Er (Error 77-80) Inter-Solutions Module comms error | Cause: Communication error between slots (1, 2, 3, or unknown). Remedy:
| SLX.Er (Error 82) Communications to drive faulty | Cause: Module-to-Drive comms failure. Remedy:
| SLX.Er Solutions Module slot X trip | Cause: Solutions Module in slot X or Digitax ST EZMotion has detected a fault. Remedy:
Common Sub-codes (Automation/EZMotion): 41-44: Parameter access errors 74: Module overheat 104: Following error 121, 125, 128, 130, 143, 154, 157, 174: File corruption (Consult factory) 175: Module output overload |
| SLX.HF Solutions Module hardware fault | Cause: Solutions Module in slot X has a hardware fault. Remedy:
| SLX.nF Solutions Module removed | Cause: Solutions Module in slot X has been removed. Remedy:
| SL.rtd Solutions Module routing error | Cause: Drive mode has changed and Solutions Module parameter routing is now incorrect. Remedy:
| SLX.tO Solutions Module watchdog timeout | Cause: Solutions Module watchdog timeout. Remedy:
| t010 User defined trip | Cause: User trip defined in 2nd processor Solutions Module code (Error 10). Remedy:
| t038 User defined trip | Cause: User trip defined in 2nd processor Solutions Module code (Error 38). Remedy:
| t040 to t089 User defined trip range | Cause: User trip defined in 2nd processor Solutions Module code (Errors 40 to 89). Remedy:
| th Motor thermistor trip | Cause: Motor temperature high or monitoring fault. Remedy:
| thS Motor thermistor short circuit | Cause: Motor thermistor wiring short circuit. Remedy:
| tunE* Autotune stopped | Cause: Autotune stopped before completion. (Error 18) Remedy:
| tunE1* Position feedback error during inertia test | Cause: The position feedback did not change or required speed could not be reached during the inertia test. (Error 11) Remedy:
| tunE2* Position feedback direction incorrect | Cause: Position feedback direction incorrect or motor could not be stopped during the inertia test. (Error 12) Remedy:
| tunE3* Commutation signal error | Cause: Drive encoder commutation signals connected incorrectly or measured inertia out of range. (Error 13) Remedy:
| tunE4* U commutation signal fail | Cause: Drive encoder U commutation signal fail during an autotune. (Error 14) Remedy:
| tunE5* V commutation signal fail | Cause: Drive encoder V commutation signal fail during an autotune. (Error 15) Remedy:
| tunE6* W commutation signal fail | Cause: Drive encoder W commutation signal fail during an autotune. (Error 16) Remedy:
| tunE7* Motor poles set incorrectly | Cause: Motor number of poles set incorrectly. (Error 17) Remedy:
| UP ACC Onboard PLC access error | Cause: Onboard PLC program: cannot access Onboard PLC program file on drive. (Error 98) Remedy:
| UP div0 PLC divide by zero | Cause: Onboard PLC program attempted divide by zero. (Error 90) Remedy:
| UP OFL PLC stack overflow | Cause: Onboard PLC program variables and function block calls using more than the allowed RAM space. (Error 95) Remedy:
| UP ovr PLC parameter write range | Cause: Onboard PLC program attempted out of range parameter write. (Error 94) Remedy:
| UP PAr PLC non-existent parameter | Cause: Onboard PLC program attempted access to a non-existent parameter. (Error 91) Remedy:
| UP ro PLC read-only write | Cause: Onboard PLC program attempted write to a read-only parameter. (Error 92) Remedy:
| UP So PLC write-only read | Cause: Onboard PLC program attempted read of a write-only parameter. (Error 93) Remedy:
| UP udF PLC un-defined trip | Cause: Onboard PLC program un-defined trip. (Error 97) Remedy:
| UP uSEr PLC requested trip | Cause: Onboard PLC program requested a trip. (Error 96) Remedy:
| UV DC bus under voltage | Cause: DC bus under voltage threshold reached. Remedy:
| HF01 to HF16 Hardware faults | Cause: These indicate serious internal problems. Remedy: Cannot be reset. The drive is inactive after one of these trips and the display shows HFxx. |
| HF17 to HF32, SL1.HF, SL2.HF, SL3.HF Non-resetable trips | Cause: Internal drive fault. Remedy: Cannot be reset. |
| EEF EEF trip | Cause: EEPROM failure or corruption. Remedy: Cannot be reset unless a code to load defaults is first entered in Pr x.00 or Pr 11.43. |
| C.Boot, C.Busy, C.Chg, C.Optn, C.Rdo, C.Err, C.dat, C.FULL, C.Acc, C.rtg, C.Typ, C.cpr, C.Prod SMARTCARD trips | Cause: Issues related to SMARTCARD operation (read/write/data). Remedy: SMARTCARD trips have priority 5 during power up. Check SMARTCARD status and data. |
| PS.24V, EnC1 Encoder power supply trips | Cause: Power supply fault for encoder. Remedy: These trips can only override the following priority 5 trips: EnC2 – EnC8 or Enc11 – En17. Check encoder wiring and supply. |
| OI.AC, OI.br, OIAC.P, OIbr.P, OidC.P Normal trips with extended reset | Cause: Overcurrent or overload conditions requiring cooldown. Remedy: Can be reset after 10.0s. |
| Old1, cL2, cL3, SCL Non-important trips | Cause: Various minor trip conditions. Remedy: If bit 0 of Pr 10.37 is 1 the drive will stop before tripping. |
| PH Phase loss | Cause: One or more input phases are missing. Remedy: The drive attempts to stop before tripping. Check input supply. |
| O.ht3 Drive over-heat based on thermal model | Cause: Thermal model suggests drive overheating. Remedy: The drive attempts to stop before tripping, but if it does not stop within 10s the drive will automatically trip. Check cooling. |
| UV Self resetting trips (Under Voltage) | Cause: Supply voltage is below specification. Remedy: Under voltage trip cannot be reset by the user, but is automatically reset by the drive when the supply voltage is with specification. |
| br.rS Braking resistor overload | Cause: Braking resistor I2t accumulator (Pr 10.39) in the drive has reached 75.0 % of the value at which the drive will trip and the braking IGBT is active. Remedy: Check braking resistor sizing and duty cycle. |
| Hot Heatsink or control board or inverter IGBT over temperature | Cause:
Remedy: Reduce load, check fans, or lower ambient temperature. |
| OVLd Motor overload | Cause: The motor I2t accumulator (Pr 4.19) in the drive has reached 75 % of the value at which the drive will be tripped and the load on the drive is >100 %. Remedy: Reduce motor load. |
| Auto tune Autotune in progress | Cause: The autotune procedure has been initialised. ‘Auto’ and ‘tunE’ will flash alternatively on the display. Remedy: Wait for autotune to complete. |
| Lt Limit switch is active | Cause: Indicates that a limit switch is active and that it is causing the motor to be stopped (i.e. forward limit switch with forward reference etc.). Remedy: Check limit switches and machine position. |
| PLC Onboard PLC program is running | Cause: An Onboard PLC program is installed and running. Remedy: Information only. The lower display will flash ‘PLC’ once every 10 s. |
| ACUU AC Supply loss | Cause: The drive has detected that the AC supply has been lost and is attempting to maintain the DC bus voltage by decelerating the motor. Remedy: Check mains supply. |
| dc DC applied to the motor | Cause: The drive is applying DC injection braking. Remedy: Status indication. |
| dEC Decelerating | Cause: The drive is decelerating the motor. Remedy: Status indication. |
| inh Inhibit | Cause: The drive is inhibited and cannot be run. The drive enable signal is not applied to terminal 31 or Pr 6.15 is set to 0. Remedy: Apply enable signal to terminal 31 or check Pr 6.15. |
| POS Positioning | Cause: The drive is positioning/orientating the motor shaft. Remedy: Status indication. |
| rdY Ready | Cause: The drive is ready to be run. Remedy: Status indication. |
| SCAn Scanning | Cause: Regen > The drive is enabled and is synchronising to the line. Remedy: Status indication. |
| StoP Stop or holding zero speed | Cause: The drive is holding zero speed. Regen > The drive is enabled but the AC voltage is too low, or the DC bus voltage is still rising or falling. Remedy: Status indication. |
| triP Trip condition | Cause: The drive has tripped and is no longer controlling the motor. Remedy: Check the trip code on the lower display and resolve the fault. |
| boot Booting | Cause: A parameter set is being transferred from the SMARTCARD to the drive during power-up. Remedy: Wait for transfer to complete. Refer to User Guide for details. |
| cArd Card Write | Cause: The drive is writing a parameter set to the SMARTCARD during power-up. Remedy: Wait for write to complete. |
| loAding Loading | Cause: The drive is writing information to a Solutions Module. Remedy: Status indication. |
Safety Note: If the drive displays a code starting with “HF” (e.g., HF08), this indicates a Hardware Fault. These represent internal power stage failures. Do not attempt to reset an HF trip multiple times, as this can cause further internal damage.
How to Read Digitax ST Faults via CTSoft & Connect
In 2026, troubleshooting a Digitax ST is most effective when using CTSoft (the legacy commissioning tool) or Control Techniques Connect software. These tools allow you to look deeper into the drive’s parameters than the 2-digit LED display allows.
- Trip History (Menu 10): The Digitax ST stores the last 10 trips in Parameters 10.20 through 10.29. Using software, you can view the “Trip Time” (measured in drive run-hours) to correlate the fault with machine events.
- SM-Option Modules: The Digitax ST features two slots for SM-Option modules (e.g., SM-Encoder, SM-Applications). If a trip occurs in a module, the drive will often display a sub-trip code to identify whether Slot 1 or Slot 2 caused the issue.
- Real-Time Monitoring: Use the software to trace Parameter 04.02 (Active Torque Reference) and 03.02 (Speed Feedback). Spikes in these values just before a trip can indicate mechanical binding or encoder signal noise.
- SmartStick: If you use a SmartStick (the green memory stick), you can easily upload the fault log and parameter set to a PC or clone it to a replacement drive for fast recovery.
Q: What is the difference between a Trip and a Warning on the Digitax ST?
A: A Trip (Solid code) is a protective shutdown that stops the motor immediately. A Warning (Flashing code) indicates the drive is nearing a limit—such as O.Ld1 (Load Warning) or Hot (Heatsink temperature)—but it will keep the motor running until the condition becomes critical.
Q: How do I reset a Digitax ST fault?
A: Once the root cause (such as a mechanical jam or cable issue) is resolved, you can reset the drive via:
- Pressing the Red Reset Button on the keypad.
- Cycling the Main Power (Wait 30 seconds for the display to go dark before reapplying power).
- Toggling a Digital Input assigned to the “Reset” function (Terminal 31 is the default enable/reset).
Q: What does “ih” mean on the display?
A: “ih” stands for Inhibit. This is a status code, not a fault. It means the drive is healthy but cannot run because the Secure Torque Off (STO) / Enable signal is missing from Terminal 31. Once 24V is applied, the display should change to “rd” (Ready).
Q: My drive shows “Enc1,” what should I check?
A: Enc1 is a Primary Encoder Fault. Check the motor encoder cable for damage, ensure the connector is securely fastened, and verify that the encoder shield is properly grounded. In high-vibration applications, the encoder itself may have failed.
Q: Where is the trip history stored?
A: The trip history is stored in the non-volatile memory in Menu 10. Parameter 10.20 always contains the most recent trip data, and this log is preserved even when the drive is powered down.