How can resolve problem A2001 alarm in ABB ACS150 ?

2 Replies
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : OVERCURRENT, Output current limit controller is active.

programmable fault function,

parameter 1610 - DISPLAY ALARMS

1. Check motor load.

2. Check acceleration time

parameters 2202 - ACCELER TIME 1 and

2205 - ACCELER TIME 2.

3. Check motor and motor cable (including phasing).

4. Check ambient conditions.

5. Load capacity decreases if installation site ambient temperature exceeds 40 °C

 

 