How can resolve problem F0001 OVERCURRENT fault in ABB ACS150 ?
2 Replies
Oct 12, 2021 12:20 pm
Cause : Output current has exceeded trip level.
1. Check motor load.
2. Check acceleration time parameters
2202 ACC TIME 1 and
2205 ACC TIME 2.
3. Check motor and motor cable (including phasing).
4. Check ambient conditions.
5. Check that the start-up data in parameter group 99 corresponds to the motor rating plate.
6. Check that there are no power factor correction capacitors or surge absorbers in motor cable.
7. Check motor cable.
8. Check drive using multimeter.