How can resolve problem F0002 DC OVERVOLT fault in ABB ACS150 ?

2 Replies
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Excessive intermediate circuit DC voltage. DC over-voltage trip limit is 420 V for 200 V drives and 840 V for 400 V drives.

1. Check that overvoltage controller is on

parameter 2005 OVERVOLT CTRL.

2. Check brake chopper and resistor (if used). DC overvoltage control must be deactivated when brake chopper and resistor are used.

3. Check deceleration time parameters

2203 DEC TIME 1 and

2206 DEC TIME 2.

4. Check input power line for static or transient overvoltage.

5. Retrofit frequency converter with brake chopper and brake resistor.