How can resolve problem F1012 PAR PFC IO 1 Fault in ABB ACS550 Drive ?
1 Reply
Dec 15, 2021 11:37 am
IO configuration is not complete – not enough relays are parameterized to PFC.
Or, a conflict exists between
Group 14: RELAY OUTPUTS,
parameter 8117 NR OF AUX MOT and
parameter 8118 AUTOCHNG INTERV