F1009 PAR PCU 1 Fault in ABB ACS550 Drive

2 Posts
1 Users
0 Reactions
8,792 Views
Posts: 20042
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago
[#1180]

How can resolve problem F1009 PAR PCU 1 Fault in ABB ACS550 Drive ?


1 Reply
Posts: 20042
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago

Parameter values for power control are inconsistent: Improper motor
nominal frequency or speed. Check for both of the following:
1 < (60 · 9907 MOTOR NOM FREQ / 9908 MOTOR NOM SPEED < 16
0.8 < 9908 MOTOR NOM SPEED /
(120 · 9907 MOTOR NOM FREQ / Motor Poles) < 0.992