2340 SHORT CIRCUIT Fault in ABB ACS800 Drive

10 Posts
5 Users
1 Reactions
15.9 K Views
Posts: 19853
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 2340 SHORT CIRCUIT Fault in ABB ACS800 Drive ?

9 Replies
Posts: 19853
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Short-circuit in motor cable(s) or motor.

Check motor and motor cable.
Check there are no power factor correction
capacitors or surge absorbers in motor cable.

Reply
2 Replies
(@jromerov)
Joined: 2 years ago

New Member
Posts: 1

@click2electro 

 

Hello there. Any other cause for this fault to occur?

Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 19853

Condition of fault coming continuously or coming after run command ?

Reply
Posts: 1
(@bharatburbure)
New Member
Joined: 2 years ago

If motor and motor cable found OK, then it was hardware fault, surely.

Reply
1 Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 19853

@bharatburbure yes it is an hardware fault.

Reply
Posts: 6
(@tahir)
Active Member
Joined: 2 years ago

It can be a fault due to shorted IGBT as well.

Reply
3 Replies
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 19853

@tahir

This fault comes when IGBT faulty, Motor Faulty, CT Faulty and faulty motor connetion

Reply
 jose
(@jose)
Joined: 9 months ago

New Member
Posts: 1

@tahir hey how did you resolve this issue please we disconnected the motor cables and the short sircuit fault is still showing 2340

Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 19853

@jose after remove motor cable if fault still coming then IGBT, ZINT board or CT faulty.

Reply