Forum

Notifications
Clear all

F0001 OVERCURRENT Fault in ABB ACS850 Drive

2 Posts
1 Users
0 Reactions
2,280 Views
Posts: 20042
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago
[#1530]

How can resolve problem F0001 OVERCURRENT Fault in ABB ACS850 Drive ?


1 Reply
Posts: 20042
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago

Cause : Output current has exceeded internal fault limit.

Check motor load.
Check acceleration times in parameter
group 22 Speed ref ramp.
Check motor and motor cable (including
phasing and delta/star connection).
Check that the start-up data in parameter
group 99 corresponds to the motor rating
plate.
Check that there are no power factor
correction capacitors or surge absorbers
in motor cable.
Check encoder cable (including
phasing).


Reply