How can resolve problem F515 M1 field exciter over current Fault In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Motor 1 field exciter overcurrent.
Check:

In case this fault happens during field exciter autotuning,
deactivate the supervision by setting 31.59 M1 field
overcurrent level = 325 %.

The setting of 31.59 M1 field overcurrent level.

The settings of the field current controller in group 28 EMF
and field current control.

The connections of the field exciter.

The insulation of cables and field winding.

The resistance of the field winding.

For fault messages at the field exciter itself (flashing LEDs),
04.26 M1 field exciter fault word and 04.36 M1 field exciter
warning word.