Inovance MD200 Drive fault codes: Find a comprehensive list of Inovance MD200 series drive fault codes and their meanings. Quickly diagnose issues and troubleshoot your MD200 VFD for efficient maintenance and minimal downtime.

Inovance MD200 Drive fault codes

Below list shows Inovance MD200 Drive fault codes:

Fault Name Panel Possible Cause Solution
Display
Overcurrent during acceleration Err02 1. A grounding fault or short circuit exists in the output circuit of the AC drive. 1. Check the motor and the relay contactor and make sure that they are not short‑ circuited.
2. The SVC control mode is adopted, and motor auto‑ tuning is not performed. 2. Set the motor parameters according to the motor nameplate and perform motor auto‑tuning.
3. The set acceleration time is too short. 3. Increase the acceleration time .
4. The overcurrent stall suppression setting is improper. 4. Ensure that overcurrent stall suppression  is enabled.The overcurrent stall action current is too high. Adjust it to a value between 120% and 160%.The overcurrent stall suppression gain  is too low. Adjust it to a value between 20 and 40.
5. The customized torque boost or V/f curve is improper. 5. Adjust the customized torque boost or V/f curve.
6. The motor is started while rotating. 6. Enable the flying start function or start the AC drive after the motor stops.
7. The AC drive suffers external interference. 7. Check whether the fault current reaches the overcurrent stall suppression current  by viewing the fault log. If not, the fault is possibly caused by external interference. In this case, find out the external interference source and rectify the fault.If no external interference source is found, the drive board or Hall device may be faulty. In this case, contact the manufacturer for replacement.
Overcurrent during deceleration Err03 1. A grounding fault or short circuit exists in the output circuit of the AC drive. 1. Check the motor and make sure that the motor is not short‑circuited or open‑ circuited.
2. The SVC control mode is adopted, and motor auto‑ tuning is not performed. 2. Set the motor parameters according to the motor nameplate and perform motor auto‑tuning.
3. The set deceleration time is too short. 3. Increase the deceleration time.
4. The overcurrent stall suppression setting is improper. 4. Ensure that overcurrent stall suppression is enabled.The overcurrent stall action current is too high. Adjust it to a value between 120% and 150%.The overcurrent stall suppression gain  is too low. Adjust it to a value between 20 and 40.
5. The power supply unit is not provided with a braking unit and no braking resistor is installed. 5. Replace the power supply unit with one that has a braking unit and install a braking resistor.
6. The AC drive suffers external interference. 6. Check whether the fault current reaches the overcurrent stall suppression current by viewing the fault log. If not, the fault is possibly caused by external interference. In this case, find out the external interference source and rectify the fault.If no external interference source is found, the drive board or Hall device may be faulty. In this case, contact the manufacturer for replacement.
Overcurrent at constant speed Err04 1. A grounding fault or short circuit exists in the output circuit of the AC drive. 1. Check the motor and make sure that the motor is not short‑circuited or open‑ circuited.
2. The SVC control mode is adopted, and motor auto‑ tuning is not performed. 2. Set the motor parameters according to the motor nameplate and perform motor auto‑tuning.
3. The overcurrent stall suppression setting is improper. 3. Ensure that overcurrent stall suppression is enabled.The overcurrent stall action current is too high. Adjust it to a value between 120% and 150%.The overcurrent stall suppression gain is too low. Adjust it to a value between 20 and 40.
4. The AC drive power rating is too low. 4. During stable running, if the running current exceeds the rated motor current or rated output current of the AC drive, replace the AC drive with one of higher power rating.
5. The AC drive suffers external interference. 5. Check whether the fault current reaches the overcurrent stall suppression current by viewing the fault log. If not, the fault is possibly caused by external interference. In this case, find out the external interference source and rectify the fault.If no external interference source is found, the drive board or Hall device may be faulty. In this case, contact the manufacturer for replacement.
Overvoltage during acceleration Err05 The input grid voltage is Adjust the input grid voltage to the normal
too high. range.
An external force drives the motor during acceleration. Cancel the external force or install a braking resistor.
The maximum rise frequency during overvoltage stall suppression is too low. Adjust it to a value between 5 Hz and
15 Hz when an external force is applied.
The overvoltage stall suppression parameters are set improperly. Ensure that the overvoltage stall suppression function  is enabled. The overvoltage stall suppression voltage  is too high. Adjust it to a value between 700 V and 770 V.
The overvoltage stall suppression frequency gain is too low. Adjust it to a value
between 30 and 50.
The power supply unit is not provided with a braking unit and no braking resistor is Replace the power supply unit with one that has a braking unit and install a braking resistor.
installed.
The acceleration time is Increase the acceleration time.
too short.
Overvoltage during deceleration Err06 The overvoltage stall suppression parameters are set improperly. Ensure that the overvoltage stall suppression function is enabled. The overvoltage stall suppression voltage is too high. Adjust it to a value between 700 V and 770 V.
The overvoltage stall suppression frequency gain is too low. Adjust it to a value
between 30 and 50.
An external force drives the motor during deceleration. Cancel the external force or install a braking resistor.
The maximum rise frequency during overvoltage stall suppression is too low. Adjust it to a value between 5 Hz and
15 Hz when an external force is applied.
The deceleration time is Increase the deceleration time.
too short.
The power supply unit is not provided with a braking unit and no braking resistor is Replace the power supply unit with one that has a braking unit and install a braking resistor.
installed.
Overvoltage at constant speed Err07 The overvoltage stall suppression parameters are set improperly. Ensure that the overvoltage stall suppression function  is enabled. The overvoltage stall suppression voltage is too high. Adjust it to a value between 700 V and 770 V.
The overvoltage stall suppression frequency
gain is too low. Adjust it to a value between 30 and 50.
An external force drives the motor during running. Cancel the external force or install a braking resistor.
The maximum rise frequency during overvoltage stall suppression is too low. Adjust it to a value between 5 Hz and
15 Hz when an external force is applied.
Err08 - Control power fault Input voltage is not within the permissible
range. 
Adjust the input voltage in the permissible range.
 
Undervoltage Err09 An instantaneous power Enable the power dip ride‑through function
failur  
The input voltage of the Adjust the input voltage of the AC drive to the normal range.
AC drive is beyond the specified range.
The bus voltage is Contact the technical support personnel.
abnormal.
The power supply unit, the drive board of the drive unit, or the control board of the drive unit Contact the technical support personnel.
is abnormal.
AC drive overload Err10 The load is too heavy or Reduce the load and check the motor and
motor stalling occurs. mechanical conditions.
The AC drive power Replace the AC drive with one of higher
rating is too low. power rating.
The SVC control mode is adopted, and motor auto‑tuning is not Set the motor parameters according to the motor nameplate and perform motor auto‑ tuning.
performed.
The control mode is V/f control. Reduce the torque boost reference in decrements of 1.0%, or set it to 0 (auto
torque boost).
Motor overload Err11 (motor overload protection gain) is set Increase its value to prolong the motor overload time.
improperly.
The load is too heavy or Reduce the load and check the motor and
motor stalling occurs. mechanical conditions.
Input voltage exception Err11 Input voltage phase loss Check the three‑phase power supply and make sure that it is normal.
Check the input cables and make sure that they are not broken.
Check the input terminals and make sure
that they are properly connected.
E12.04 The input three‑phase voltage is too high. Ensure that the input voltage does not exceed the rated value:
Three‑phase 380 V models: 576 V
Single‑phase 220 V models: 288 V
Output phase loss Err13 The motor is faulty. Check the motor for open circuit.
The cable connecting the AC drive and the Check the cable between the AC drive and the motor.
motor is abnormal.
The three‑phase outputs of the AC drive are unbalanced when Check whether the motor three‑phase winding is normal. If not, eliminate the fault.
the motor is running.
The drive board or the Contact the technical support personnel.
IGBT is abnormal.
IGBT overheat Err14 The ambient Lower the ambient temperature.
temperature is too high.
The air filter is blocked. Clean the air filter.
The fan is damaged. Replace the fan.
The thermistor of the Contact the technical support personnel.
IGBT is damaged.
The IGBT is damaged. Contact the technical support personnel.
External device fault Err15 An external fault signal Eliminate the external fault, ensure that the
is input through multi‑ functional DI (NO). mechanical condition allows restart , and reset the operation.
  An external fault signal Eliminate the external fault, ensure that the
is input through the multi‑functional DI (NC). mechanical condition allows restart (, and reset the operation.
  Err16 Modbus communication timeout Check whether the Modbus master sends data within the set timeout period.
Check whether the RS485 circuit is
disconnected or suffers interference.
Err18 Current detection
fault
The drive board is abnormal.
     
     
 
     
 
 
     
 
     
   
     
 
     
 
 
     
     
 
     
 
     
 
 