A0505 alarm in siemens micromaster 420 or MM420 drive

2 Posts
1 Users
0 Likes
180 Views
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

A0505 alarm in siemens micromaster 420 or MM420 drive - comes when overload alarm limit P0294 is exceeded or the pulse frequency and/or the output frequency is reduced.

1 Reply
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Inverter I2T - when overload alarm limit P0294 is exceeded or the pulse frequency and/or the output frequency is reduced.

1. Overload alarm limit P0294 is exceeded (refer to utilization r0036)

2. The pulse frequency and/or the output frequency is reduced as a function of the setting of parameter P0290

3.Check whether the load duty cycle lies within the permissible limits.