How can resolve problem A2001 alarm in ABB ACS150 ?
2 Replies
Oct 19, 2021 6:42 am
Cause : OVERCURRENT, Output current limit controller is active.
programmable fault function,
parameter 1610 - DISPLAY ALARMS
1. Check motor load.
2. Check acceleration time
parameters 2202 - ACCELER TIME 1 and
2205 - ACCELER TIME 2.
3. Check motor and motor cable (including phasing).
4. Check ambient conditions.
5. Load capacity decreases if installation site ambient temperature exceeds 40 °C