Sinamics G120 fault F7802 showing

2 Posts
2 Users
0 Reactions
332 Views
Posts: 12
 sam
Topic starter
(@sam)
Eminent Member
Joined: 3 months ago
[#20365]

i have issue with sinamics G120 drive showing fault F7802 continuously. After several time power on off drive showing shame issue. Please suggest any solution for this fault.


1 Reply
Posts: 20042
Admin
(@click2electro)
Member
Joined: 5 years ago

In Sinamics G120 fault F7802 indicates " Power Unit Not Ready," meaning the Control Unit (CU) cannot detect or communicate with the Power Module (PM).

  • This is commonly caused by loose connections, missing 24V supply to the power unit (especially for larger frames), or faulty power hardware.

Reply