4290 Cooling Fault in ABB ACS880 Drive

3 Posts
1 Users
0 Reactions
2,056 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 4290 Cooling Fault in ABB ACS880 Drive ?

2 Replies
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Drive module temperature is excessive.

1. Check ambient temperature. If it exceeds 40 °C (104 °F), ensure that load current does not exceed derated load capacity of drive.

2. Check drive module cooling air flow and fan operation.

3. Check inside of cabinet and heatsink of drive module for dust pick-up.

4. Clean whenever necessary.