5093 Rating ID mismatch Fault in ABB ACS880 Drive

5 Posts
2 Users
0 Reactions
7,565 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 5093 Rating ID mismatch Fault in ABB ACS880 Drive ?

4 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The hardware of the drive does not match the information stored in the memory unit. This may occur eg. after a firmware update or memory unit replacement.

This fault also coming if you change power card or control card.

1. Reset fault.

2. Restart drive.

 

Reply
Posts: 18330
Posts: 1
 anis
(@anis)
New Member
Joined: 1 year ago

I am experiencing the same problem. Installed memory unit is primary control. I have new memory unit which is spinning control. Is it possible to program it to primary control. 

Reply
1 Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 18330

@anis after install new memory restart drive if fault comes after restart then only ABB help for this fault.

Reply