How can resolve problem 5093 Rating ID mismatch Fault in ABB ACS880 Drive ?
4 Replies
Dec 13, 2021 9:25 am
Cause : The hardware of the drive does not match the information stored in the memory unit. This may occur eg. after a firmware update or memory unit replacement.
This fault also coming if you change power card or control card.
1. Reset fault.
2. Restart drive.
Jun 29, 2023 6:40 am
Other Useful Link For ACS880 Drive
Nov 21, 2023 10:21 am
I am experiencing the same problem. Installed memory unit is primary control. I have new memory unit which is spinning control. Is it possible to program it to primary control.