Forum

Share:
Notifications
Clear all

7510 FBA A communication Fault in ABB ACS880 Drive

3 Posts
1 Users
0 Reactions
14.2 K Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 7510 FBA A communication Fault in ABB ACS880 Drive ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Cyclical communication between drive and fieldbus adapter module A or between PLC and fieldbus adapter module A is lost.

1. Check status of fieldbus communication. See user documentation of fieldbus interface.

2. Check settings of parameter groups 50 Fieldbus adapter (FBA), 51 FBA A settings, 52 FBA A data in and 53 FBA A data out.

3. Check cable connections.

4. Check if communication master is able to communicate.

Reply
Posts: 18330
Share: