A6E5 AI parametrization warning in ABB ACS880 Drive

3 Posts
1 Users
0 Reactions
2,330 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A6E5 AI parametrization warning in ABB ACS880 Drive ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause: The current/voltage jumper setting of an analog input does not correspond to parameter settings.

1. Adjust either the jumper setting (on the drive control unit) or parameter

12.15/12.25.

Note: Control board reboot (either by cycling the power or through parameter96.08 - Control board boot) is required to validate any changes in the jumper settings.

Parameter setting for analog input source type voltage or mA

12.15 - V or mA

12.25 - V or mA

If you select V (Voltage) and drive received mA signal at analog input or if you select mA and drive received V (Voltage)signal at analog input then this fault comes so change 12.15 and 12.25 according to analog input signal.