Forum

Notifications
Clear all

6681 EFB comm loss Fault in ABB ACS880 Drive

3 Posts
1 Users
0 Reactions
4,011 Views
Posts: 20293
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago
[#930]

How can resolve problem 6681 EFB comm loss Fault in ABB ACS880 Drive ?


2 Replies
Posts: 20293
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago

Cause : Communication break in embedded fieldbus (EFB) communication.

1. Check the status of the fieldbus master (online/offline/error etc.).

2. Check cable connections to the EIA-485/X5 terminals 29, 30 and 31 on the control unit.


Reply