How can resolve problem A7A2 Mechanical brake opening failed warning in ABB ACS880 Drive ?
Cause : Status of mechanical brake acknowledgement is not as expected during brake open.
1. Programmable warning:
44.17 -Â Brake fault function.
2. Check mechanical brake connection.
3. Check mechanical brake settings in parameter group 44 Mechanical brake control.
4. Check that acknowledgement signal matches actual status of brake.