How can resolve problem 65A1 FBA A parameter conflict Fault in ABB ACS880 Drive ?
2 Replies
Dec 13, 2021 10:13 am
Cause : The drive does not have a functionality requested by PLC, or requested functionality has not been activated.
1. Check PLC programming.
2. Check settings of parameter groups 50 Fieldbus adapter (FBA) and 51 FBA A settings.